Electrocution Cases
25.
Electrocution of Nine Passengers in Saiha District, Mizoram
(Case No. 8/16/0/2011)
4.183 The Commission received a complaint that a passenger bus carrying 36 passengers
came in contact with a live overhead electric cable between New Serkawr and New Latawh
in Saiha District of Mizoram on 25 March 2011 causing death of nine passengers.
4.184 According to the report received from the Under Secretary to the Government of
Mizoram (Power and Electricity Department), there were many shortcomings in the
maintenance of the electric lines. For instance :
(i)
11 KV overhead line ran dangerously low above the road.
(ii)
The vertical cable of the 11 KV conductor above the ground was 3.35 meter
whereas it should not be less than 4.5 meters.
(iii)
The double pole supporting the line was leaning to the extent of 30 degrees. It
was so because the pole was not supported by a stay and was found uprooted
from the ground. This reduced the vertical clearance from the ground.
(iv)
Had the stay for the double pole location been intact, the consequent lowering
of the conductor would not have happened and the tragic incident could have
been avoided.
(v)
The 11 KV line was constructed during the year 1993-1994 when there was
only fair-weather jeep road in the area. Improvement of this road was taken
up by the PWD in the year 2009 and it was likely that the stay for the double
pole was uprooted while carrying out earth excavation on the road.
4.185 The report also revealed that some utensils piled up on the top of the bus came in
contact with the 11 KV overhead line.
4.186 Another report dated 7 December 2011 was also received from the Under Secretary
to the Government of Mizoram (Home Department) forwarding a magisterial inquiry report
and informed that financial assistance of ` 10,000 each was given to the families of the nine
deceased persons. It also informed that the police has registered a case which is under
investigation.
4.187 The Inquiry Magistrate found that the electric cable was hanging low and due to
the heavy cyclone which lashed the area a week before may be the reason for the same.
During the investigation it was found that since the Junior Engineer (P&E Division),
Lawngtlai, In-charge of the 11 KV line was responsible for gross negligence in maintaining
the line, the case is pending for his arrest since he is out of station.